Step 1: Objective of the Test:
The Open Circuit (OC) or No-Load test is performed on a transformer to determine:
Core losses (Iron losses), which consist of hysteresis and eddy current losses.
No-load parameters ($R_0$ and $X_0$).
Step 2: Experimental Circuit Setup:
Winding Configuration: The High Voltage (HV) winding of the transformer is kept completely open-circuited, while all measuring instruments are connected to the Low Voltage (LV) winding. This is done because it is safer and easier to apply rated voltage on the LV side.
Instruments Connected:
A voltmeter (across the input to measure rated LV voltage, $V_0$).
An ammeter (in series to measure no-load current, $I_0$).
A Low Power Factor (LPF) wattmeter (to measure no-load input power, $W_0$).
Applied Input: Rated voltage at rated frequency is applied to the LV winding.
Step 3: Test Analysis:
Since the secondary side is open, the current drawn ($I_0$) is very small (typically $2\%\text{ to }5\%$ of full-load current). Thus, copper losses ($I_0^2 R$) in the primary are negligible. The wattmeter reading ($W_0$) therefore directly measures the constant core losses ($W_c$):
$$W_0 \approx \text{Core/Iron Loss } (W_c)$$