Question:

A factory has a load of \(400\ \text{kW}\) at a power factor of \(0.8\) lagging. If the power factor is to be improved to unity, the required KVAR of the capacitor bank is

Show Hint

For power factor correction, capacitor KVAR is \(P(\tan\phi_1-\tan\phi_2)\).
Updated On: May 27, 2026
  • \(400\ \text{KVAR}\)
  • \(300\ \text{KVAR}\)
  • \(500\ \text{KVAR}\)
  • \(100\ \text{KVAR}\)
Show Solution
collegedunia
Verified By Collegedunia

The Correct Option is B

Solution and Explanation

Concept: Reactive power compensation required for power factor correction is: \[ Q_c=P(\tan\phi_1-\tan\phi_2) \] where \(\phi_1\) is initial power factor angle and \(\phi_2\) is final power factor angle.

Step 1:
Given active power: \[ P=400\ \text{kW} \] Initial power factor: \[ \cos\phi_1=0.8 \]

Step 2:
Find \(\sin\phi_1\). \[ \sin\phi_1=\sqrt{1-\cos^2\phi_1} \] \[ \sin\phi_1=\sqrt{1-0.8^2} \] \[ \sin\phi_1=\sqrt{1-0.64} \] \[ \sin\phi_1=0.6 \]

Step 3:
Find \(\tan\phi_1\). \[ \tan\phi_1=\frac{\sin\phi_1}{\cos\phi_1} \] \[ \tan\phi_1=\frac{0.6}{0.8}=0.75 \]

Step 4:
Final power factor is unity: \[ \cos\phi_2=1 \] So: \[ \phi_2=0^\circ \] \[ \tan\phi_2=0 \]

Step 5:
Calculate capacitor KVAR. \[ Q_c=P(\tan\phi_1-\tan\phi_2) \] \[ Q_c=400(0.75-0) \] \[ Q_c=300\ \text{KVAR} \] Therefore: \[ \boxed{300\ \text{KVAR}} \]