Question:

A symmetrical 3-phase fault occurs at a bus. If the pre-fault voltage is 1.0pu and the Thevenin impedance is j0.2pu, the fault current in per-unit is:

Show Hint

For any symmetrical fault, the fault current is inversely proportional to the Thevenin impedance.
If \(Z_{\text{th}} = jX\), the magnitude of the fault current is simply \(1/X\) (for \(V_{\text{th}} = 1.0\)).
Here, \(1 / 0.2 = 5.0\text{ pu}\). This calculation can be performed mentally in seconds.
Updated On: Jul 4, 2026
  • 0.2pu
  • 2.0pu
  • 5.0pu
  • 10.0pu
Show Solution
collegedunia
Verified By Collegedunia

The Correct Option is C

Solution and Explanation

Step 1: Understanding the Question:
The question asks for the per-unit (pu) magnitude of the short-circuit fault current during a symmetrical three-phase fault at a busbar, given the pre-fault voltage and the Thevenin impedance at that bus.

Step 2: Key Formula or Approach:

Using the Thevenin equivalent circuit at the fault location, the fault current (\(I_f\)) in per-unit is given by:
\[ I_f = \frac{V_{\text{th}}}{Z_{\text{th}}} \] where:
- \(V_{\text{th}}\) is the pre-fault Thevenin voltage at the bus (usually \(1.0\text{ pu}\)).
- \(Z_{\text{th}}\) is the equivalent Thevenin impedance of the network seen from the faulted bus.

Step 3: Detailed Explanation:


• Identify the given parameters:
- Pre-fault voltage, \(V_{\text{th}} = 1.0\text{ pu}\).
- Thevenin impedance, \(Z_{\text{th}} = j0.2\text{ pu}\).

• Substitute these values into the fault current formula:
\[ I_f = \frac{1.0}{j0.2} \]
• Simplify the expression:
\[ I_f = -j \left(\frac{1.0}{0.2}\right) = -j5.0\text{ pu} \]
• Calculate the magnitude of the fault current:
\[ |I_f| = 5.0\text{ pu} \]

Step 4: Final Answer:

The fault current in per-unit is 5.0pu.