Concept:
Transformer short circuit test is mainly performed to determine:
• copper losses,
• equivalent impedance,
• equivalent resistance and reactance.
Core loss is determined using the open circuit test, not the short circuit test.
Step 1: Understanding short circuit test arrangement.
In short circuit test:
• one winding is short circuited,
• low voltage is applied to the other winding,
• rated current is allowed to flow.
Usually:
\[
\text{LT winding is short circuited}
\]
for convenience and safety.
Step 2: Checking statement (1).
Statement:
\[
\text{It is used to find copper losses}
\]
This is correct.
During short circuit test:
• applied voltage is very small,
• flux produced is very small,
• iron loss becomes negligible.
Hence wattmeter reading approximately equals copper loss.
Step 3: Checking statement (2).
Statement:
\[
\text{LT winding is usually short circuited}
\]
This is correct because:
• LT winding carries high current,
• HV side requires smaller current supply for testing,
• practical handling becomes easier.
Step 4: Checking statement (3).
Statement:
\[
\text{It is used to determine core loss}
\]
This is incorrect.
Core loss is measured using:
\[
\text{Open circuit test}
\]
not short circuit test.
In short circuit test, flux is very low and iron loss is negligible.
Step 5: Checking statement (4).
Statement:
\[
\text{Short circuit test is performed at rated current}
\]
This is correct.
The applied voltage is adjusted until:
\[
I=I_{\text{rated}}
\]
Hence statement (4) is correct.
Step 6: Selecting the incorrect statement.
The incorrect statement is:
\[
\boxed{(3)}
\]