Concept:
In power system load flow analysis:
• PV bus is also called generator bus,
• real power \(P\) and voltage magnitude \(|V|\) are specified,
• reactive power \(Q\) is calculated.
However, generators cannot supply unlimited reactive power.
When reactive power exceeds generator limits, the PV bus is converted into a PQ bus.
Step 1: Understanding PV bus.
For a PV bus:
\[
P = \text{specified}
\]
\[
|V| = \text{specified}
\]
Unknown quantities are:
\[
Q \text{ and } \delta
\]
Generator excitation system controls voltage magnitude.
Step 2: Understanding reactive power limits.
Generators have limits:
\[
Q_{min} \le Q \le Q_{max}
\]
These limits are due to:
• rotor heating,
• stator current limitations,
• stability restrictions.
Step 3: What happens when limits are violated?
If calculated reactive power becomes:
\[
Q > Q_{max}
\]
or
\[
Q < Q_{min}
\]
then generator can no longer maintain specified voltage magnitude.
Hence:
• voltage control is lost,
• bus can no longer behave as PV bus.
Step 4: Conversion of bus type.
Under reactive power limit violation:
\[
\text{PV Bus} \rightarrow \text{PQ Bus}
\]
Now:
\[
P \text{ and } Q
\]
are fixed quantities and voltage magnitude is computed.
Step 5: Selecting the correct answer.
Thus PV bus is treated as PQ bus when:
\[
\text{Reactive power goes beyond limits}
\]
Hence correct option is:
\[
\boxed{(1)}
\]