Step 1: Understanding the Question:
The question asks how to increase the refrigerating effect in a reversed Brayton refrigeration cycle (also known as the Bell-Coleman or air refrigeration cycle).
Step 2: Key Formula or Approach:
The refrigerating effect (\(q_{\text{in}}\)) per unit mass of air is given by:
\[ q_{\text{in}} = C_{\text{p}} \left( T_1 - T_4 \right) \]
where \(T_1\) is the temperature of the air entering the compressor (refrigerated space temperature) and \(T_4\) is the temperature of the air leaving the expander and entering the cold cabin.
Step 3: Detailed Explanation:
• For a fixed temperature at the expander inlet (\(T_3\)), the expander outlet temperature \(T_4\) is related to the pressure ratio \(r_{\text{p}}\) by:
\[ T_4 = \frac{T_3}{r_{\text{p}}^{\frac{\gamma-1}{\gamma}}} \]
• An increase in the pressure ratio \(r_{\text{p}}\) increases the temperature difference across the expander, which can lower \(T_4\).
• However, in a complete closed cycle with fixed heat rejection and absorption temperatures, the optimal pressure ratio for maximum refrigeration capacity is relatively low.
• When the pressure ratio decreases toward this optimal operating range, the compressor discharge temperature \(T_2\) decreases, which allows for more effective cooling in the heat exchanger before expansion.
• This reduced temperature at the expander inlet (\(T_3\)) lowers \(T_4\), which increases the net refrigerating effect (\(T_1 - T_4\)) per unit of work input.
• Decreases in compressor or turbine efficiencies (Options C and D) introduce irreversibilities that always reduce cycle performance.
Step 4: Final Answer:
The refrigerating effect is increased if the pressure ratio decreases.