Step 1: Understanding the Question:
This question focuses on the performance optimization of an air refrigeration cycle (such as the Bell-Coleman or Reverse Brayton cycle).
We need to determine which temperature change improves the Coefficient of Performance (COP).
Step 2: Key Formula or Approach:
For an air refrigeration cycle, the COP is given by:
\[ \text{COP} = \frac{\text{Refrigeration Effect}}{\text{Net Work Input}} = \frac{T_1 - T_4}{(T_2 - T_1) - (T_3 - T_4)} \]
where:
$T_1$ is the compressor inlet temperature,
$T_2$ is the compressor outlet temperature,
$T_3$ is the turbine inlet temperature, and
$T_4$ is the turbine outlet (exit) temperature.
Step 3: Detailed Explanation:
• The refrigeration effect occurs as the air passes through the evaporator/cabin, absorbing heat. This effect is proportional to $T_1 - T_4$.
• Lowering the turbine exit temperature ($T_4$) directly increases the temperature difference ($T_1 - T_4$), thereby increasing the refrigeration effect.
• Additionally, a lower $T_4$ expands the temperature range over which heat is absorbed, leading to more effective cooling per unit of work done.
• Consequently, a lower turbine exit temperature improves the overall COP of the cycle.
Step 4: Final Answer:
The COP of an air refrigeration cycle improves when the turbine exit temperature decreases.