The heat duty (Q) for the heat exchanger is given by the equation:
\[
Q = m \cdot c \cdot \Delta T
\]
Where:
\( m = 70 \, {kg/min} = \frac{70}{60} \, {kg/s} = 1.167 \, {kg/s} \)
\( c_{{water}} = 4.2 \, {kJ/(kg°C)} \)
\( \Delta T_{{water}} = 65 - 25 = 40^\circ C \)
Now, calculate the heat duty:
\[
Q = 1.167 \cdot 4.2 \cdot 40 = 196.1 \, {W}
\]
For a counter-flow heat exchanger, the heat exchanger area \( A \) can be calculated using the equation:
\[
Q = U \cdot A \cdot \Delta T_{{lm}}
\]
Where:
\( \Delta T_{{lm}} \) is the log mean temperature difference (LMTD).
For a counter-flow heat exchanger:
\[
\Delta T_{{lm}} = \frac{(T_{{in, hot}} - T_{{out, cold}}) - (T_{{out, hot}} - T_{{in, cold}})}{\ln\left(\frac{T_{{in, hot}} - T_{{out, cold}}}{T_{{out, hot}} - T_{{in, cold}}}\right)}
\]
Substitute the given values:
\[
\Delta T_{{lm}} = \frac{(110 - 65) - (65 - 25)}{\ln\left(\frac{110 - 65}{65 - 25}\right)} = \frac{45 - 40}{\ln\left(\frac{45}{40}\right)} = \frac{5}{\ln(1.125)} \approx 15.2^\circ C
\]
Now, solve for the area \( A \):
\[
A = \frac{Q}{U \cdot \Delta T_{{lm}}} = \frac{196.1}{300 \cdot 15.2} = 15.2 \, {m²}
\]