Step 1: Recall the load combinations as per IS 456:2000.
Typical factored load combinations include
\[
1.5(DL+LL),
\]
\[
1.5(DL+WL),
\]
\[
1.2(DL+LL+WL),
\]
\[
0.9DL+1.5WL,
\]
and corresponding combinations with earthquake load (EQ).
Step 2: Identify the incorrect combination.
Wind load and earthquake load are not simultaneously considered with a factor of \(1.5\) each in the same load combination.
Therefore,
\[
\boxed{
1.5DL+1.5WL+1.5EQL
}
\]
is not a valid design load combination.
Hence,
\[
\boxed{(B)}
\]
is the correct answer.