Concept:
Per-unit normalization expresses system parameters as dimensionless fractions of defined base values. The per-unit value of any impedance is calculated using the formula:
\[
Z_{pu} = \frac{Z_{\text{actual}}(\Omega)}{Z_{\text{base}}(\Omega)}
\]
The base impedance ($Z_{\text{base}}$) can be derived from the base power ($MVA_{\text{base}}$) and base line-to-line voltage ($kV_{\text{base}}$) using the standard power-voltage relationship:
\[
Z_{\text{base}} = \frac{(kV_{\text{base}})^2}{MVA_{\text{base}}}
\]
Step 1: Extract the given parameters from the text.
* Actual resistance value (\(Z_{\text{actual}}\)) = \(2\text{ }\Omega\)
* Base Power (\(MVA_{\text{base}}\)) = \(100\text{ MVA}\)
* Base Voltage (\(kV_{\text{base}}\)) = \(10\text{ kV}\)
Step 2: Calculate the base impedance (\(Z_{\text{base}}\)).
Using the formula for base impedance:
\[
Z_{\text{base}} = \frac{(10\text{ kV})^2}{100\text{ MVA}}
\]
\[
Z_{\text{base}} = \frac{100}{100} = 1\text{ }\Omega
\]
Step 3: Calculate the per-unit value (\(Z_{pu}\)).
Now, divide the actual resistance value by the calculated base impedance:
\[
Z_{pu} = \frac{2\text{ }\Omega}{1\text{ }\Omega} = 2\text{ pu}
\]
The calculated per-unit value is exactly 2, which corresponds to Option (A).