The incremental cost curves of two generators (\( \text{Gen A} \) and \( \text{Gen B} \)) in a plant supplying a common load are shown. If the incremental cost of supplying the common load is \( \lambda = 7400 \, \text{Rs/MWh} \), the common load in MW is ________________ (rounded to the nearest integer).
Given:
\( \lambda = 7400 \; \text{Rs/MWh} \)
Incremental cost equations:
For generator A:
\( I_{CA}(P_{GA}) = \dfrac{2000}{100} P_{GA} + 8000 = 20P_{GA} + 8000 \)
For generator B:
\( I_{CB}(P_{GB}) = 40P_{GB} + 6000 \)
Apply equal incremental cost criterion
\( \lambda = I_{CA} = I_{CB} = 7400 \)
For generator A:
\( 20P_{GA} + 8000 = 7400 \)
\( P_{GA} = -30 \;\text{MW} \)
Since generation cannot be negative:
\( P_{GA} = 0 \)
For generator B:
\( 40P_{GB} + 6000 = 7400 \)
\( P_{GB} = \dfrac{7400 - 6000}{40} = 35 \;\text{MW} \)
Total load supplied:
\( P_{GA} + P_{GB} = 0 + 35 = \mathbf{35 \; MW} \)
Final Answer:
The common load is 35 MW.