Concept:
The steady-state real power ($P$) developed per phase by a cylindrical-rotor synchronous machine (neglecting armature resistance $R_a$) is derived from its equivalent electrical circuit model and phasor diagram.
The mathematical expression for the total three-phase active real power is given by:
$$P = \frac{3 \cdot V \cdot E}{X_s} \cdot \sin\delta$$
Where:
• $V$ = Terminal phase voltage
• $E$ = Induced excitation EMF per phase
• $X_s$ = Synchronous reactance per phase
• $\delta$ = Load angle (or power angle/torque angle), which represents the physical magnetic displacement between the rotor and stator magnetic fields.
Step 1: Examine the variables in the power equation.
In standard operating conditions, the terminal voltage $V$ provided by the grid is constant, the synchronous reactance $X_s$ is a constant parameter of the winding geometry, and the excitation voltage $E$ is held constant for a fixed field current. Therefore, the term $\frac{3VE}{X_s}$ can be replaced by a constant value $P_{\max}$:
$$P = P_{\max} \cdot \sin\delta$$
Step 2: Determine the direct proportionality relation.
From the simplified equation, it is clear that the real power $P$ varies dynamically with the sine of the load angle:
$$P \propto \sin\delta$$
This shows that real power is directly proportional to $\sin\delta$, which corresponds to option (2).