Concept:
The electrical burden of an instrument transformer refers to the total connected load across its secondary terminal output ports, expressed in Volt-Amperes (VA). For a Current Transformer (CT), this burden power is determined by the secondary winding current flowing through the secondary load circuit impedance:
\[
\text{Burden (VA)} = (I_s)^2 \cdot Z_b
\]
where:
• \(I_s\) is the rated secondary current flowing in the circuit.
• \(Z_b\) is the total burden impedance across the secondary side.
Step 1: Identify the secondary operating parameters.
From the given current transformer nominal rating ratio:
\[
\text{Ratio} = \frac{500}{5} = \frac{\text{Primary Rated Current}}{\text{Secondary Rated Current}}
\]
Thus, the rated secondary current is:
\[
I_s = 5\text{ A}
\]
Step 2: Calculate the burden impedance (\(Z_b\)).
The given secondary burden rating value is 2 VA. Using the formula:
\[
\text{VA Burden} = I_s^2 \cdot Z_b
\]
Substitute the known values into the equation:
\[
2 = (5)^2 \cdot Z_b
\]
\[
2 = 25 \cdot Z_b
\]
Isolating the variable \(Z_b\):
\[
Z_b = \frac{2}{25}\ \Omega
\]
To express this as a decimal value, multiply both the numerator and the denominator by 4:
\[
Z_b = \frac{2 \times 4}{25 \times 4} = \frac{8}{100} = 0.08\ \Omega
\]
This calculated value corresponds to option (A).