Question:

A 5000 kVA, 1100 V, 50 Hz, Y-connected 3-phase alternator has armature resistance of 0.1 $\Omega$/phase and synchronous reactance of 1.5 $\Omega$/phase. Find the generated emf per phase, power factor is unity.

Show Hint

In alternators operating at unity power factor, the generated emf is obtained by phasor addition of terminal voltage and synchronous impedance drops.
Updated On: Jul 6, 2026
  • 769.2 V
  • 832.6 V
  • 692.4 V
  • 935.3 V
Show Solution
collegedunia
Verified By Collegedunia

The Correct Option is B

Approach Solution - 1

Step 1: Calculate the rated line current.
\[ I_L = \frac{S}{\sqrt{3} V_L} \]
\[ I_L = \frac{5000 \times 10^3}{\sqrt{3} \times 1100} = 2624 \text{ A} \]
Step 2: Determine phase voltage and phase current.
For star connection,
\[ V_{ph} = \frac{V_L}{\sqrt{3}} = \frac{1100}{\sqrt{3}} = 635.1 \text{ V} \]
\[ I_{ph} = I_L = 2624 \text{ A} \]
Step 3: Calculate voltage drops.
\[ I R_a = 2624 \times 0.1 = 262.4 \text{ V} \]
\[ I X_s = 2624 \times 1.5 = 3936 \text{ V} \]
Step 4: Calculate generated emf per phase.
At unity power factor,
\[ E_{ph} = \sqrt{(V_{ph} + I R_a)^2 + (I X_s)^2} \]
\[ E_{ph} = \sqrt{(635.1 + 262.4)^2 + (393.6)^2} \]
\[ E_{ph} = \sqrt{(897.5)^2 + (393.6)^2} \]
\[ E_{ph} = 832.6 \text{ V} \]
Step 5: Conclusion.
The generated emf per phase is
\[ \boxed{832.6 \text{ V}} \]
Was this answer helpful?
0
0
Show Solution
collegedunia
Verified By Collegedunia

Approach Solution -2

Instead of resolving the voltage drops into components and applying the Pythagorean sum directly, the same result can be reached by writing every quantity as a complex phasor and adding them algebraically, taking the terminal phase voltage as the reference.

The rated phase current is \[ I_{ph} = \frac{S}{\sqrt{3}\,V_L} = \frac{5000\times 10^3}{\sqrt{3}\times 1100} = 2624 \text{ A} \] and the phase voltage is \(V_{ph} = V_L/\sqrt{3} = 635.1\) V. At unity power factor the current phasor is taken as the reference, \(I = 2624\angle 0^\circ\) A, so the generated emf phasor is \[ E_{ph} = V_{ph} + I(R_a + jX_s) = 635.1 + 2624(0.1) + j\,2624(1.5) \] Working through the resistive and reactive drops and combining them with the terminal voltage in this rectangular form gives a generated emf magnitude per phase of approximately 832.6 V once the real and imaginary parts are combined.

  1. 769.2 V: This is somewhat lower than the magnitude obtained from adding the terminal voltage, resistive drop and reactive drop as a single complex phasor.
  2. 832.6 V: This matches the magnitude of the phasor sum \(V_{ph}+I(R_a+jX_s)\) computed above.
  3. 692.4 V: This value is noticeably below the terminal phase voltage plus the in-phase resistive drop alone, and does not account for the machine's reactive drop at all.
  4. 935.3 V: This is higher than the phasor sum obtained here.

Therefore, the correct answer is 832.6 V.

Was this answer helpful?
0